1-EN-100731-1.2
User manual
Introduction
This user manual is intended to familiarize service personnel with the design, principle of operation, structure, operation and maintenance of the pulse counter СИ30 (further in the text called «device»).
Connection, setup and maintenance should be made only by qualified specialists after reading this manual.
The device is produced in various modifications, that are encrypted in code of full conventional designation.
Power supply:
  • 220 – 90...250 V AC, 50 Hz;
  • 24 – 10,5...30 V DC.
Construction type:
  • Н – wall-mounting housing;
  • Щ1 – panel-mounting housing (square front panel, 96x96 mm);
  • Щ2 – panel-mounting housing (rectangular front panel, 96x48 mm).
Built-in outputs:
  • Р – electromagnetic relay;
  • К – transistor optocoupler of n-p-n type;
  • С – triac optocoupler.
The example of designation used for ordering and in other products documentation:
Pulse counter СИ30-220.Щ2.Р ТУ 4278-007-46526536-2010.
Safety instructions
Following symbols and keywords are used in this manual:
Danger
Keyword DANGER is used to warn about an imminent threat to health. Possible consequences may include death, permanent or prolonged incapacity for work.
Caution
Keyword CAUTION is used to prevent a potentially dangerous situation. Possible consequences may include minor injuries.
Notice
Keyword NOTICE is used for supplement, clarifying, interpretation of the main text and/or clarifying specific aspects of working the device operation.
Note
NOTE indicates helpful tips and recommendations, as well as information for efficient and trouble-free operation.
Purpose and functions
The device is a universal counter that can be used for a wide range of automation tasks. It is designed to count the number of pulses coming to its inputs in direct and opposite direction and to convert further this number into a physical value (using multiplication by given multiplier).
The device can perform following functions:
  • count-up, count-down, reversing and other types of counting pulses from the connected sensors;
  • determination of the direction of rotational motion of units and mechanisms;
  • converting the number of pulses into real units of measurement;
  • powering sensors from the built-in 24 V DC power source;
  • load control by two built-in outputs;
  • saving counting results when power is turned off;
  • connection to PC via embedded RS-485 and USB interfaces.
Specifications and operating conditions
Specifications
Main specification of the device is given in Table.
Device features
Item
Value
Power supply
AC:
  • supply voltage
  • frequency
90...250 V
(nominal - 110, 220 or 240 V)
47...63 Hz (nominal - 50 and 60 Hz)
DC
10.5...30 V
Power consumption, max.
12.5 VA
Inputs
Number of control inputs
Logical 0
0...4 V
Logical 1
10...30 V
Current for sensor’s polling
2 mA
Nominal supply voltage of the sensors
24 V
Instability of sensor supply voltage
10 %
Load current for power supply of sensors, max.
100 mA
Outputs
Number of outputs
Current switched by relay contacts, max.
8 A (220 V AC, cos φ > 0.4)
Current of transistor optocoupler load, max.
0.2 A (at 50 V)
Current of optotriac load, max.:
- at 240 V (constantly open triac)
- if the triac is switched on with frequency = 50 Hz max and timp = 5 ms
50 mA
0.5 A
Pulse counter
Number of display digits
6
Counting speed, max.
10 000 Hz
Duration of input pulses, min.
50 µs
Range of values of the multiplier
from 0.00001 to 99999
Frequency of input filter
from 1 to 50000 Hz
Pulse ratio, min.
Limit of permissible basic error (according to GOST 24907)
±1 junior digit
Basic reduced error for measurement of time intervals
±1% from 0.1 to 999.99 сtr
Housing
Dimensions:
• wall-mounting Н
• panel-mounting Щ1
• panel-mounting Щ2
105х130х65 mm
96х96х70 mm
96х48х100 mm
Protection class:
• wall-mounting Н
• panel-mounting Щ1 and Щ2
IP44
IP54 (front panel side)
Device features
Weight, max.
1 kg
Average service life
8 years
Calibration interval
2 years
Operating conditions
The device must be used in following conditions:
  • closed explosion-proof areas without aggressive vapors and gases;
  • ambient temperature from -20 to +70 °С;
  • upper limit of relative humidity = max. 95% at 35°C and lower temperatures without moisture condensation;
  • atmospheric pressure from 84 to 106.7 kPa.
In terms of resistance to mechanical influences during operation the device corresponds to group of performance N2 in GOST R 52931-2008.
Notice
It is necessary to comply with the requirements for operating conditions, as they are part of safety measures.
Safety measures
Caution
The terminal block has life-threatening voltage up to 250 V. Any connections to the device and maintenance work should be carried out only when the power is turned off.
By the method of protection from electric shock the device corresponds to class II according to GOST 12.2.007.0-75.
While operating, maintaining and checking, it is necessary to comply with GOST 12.3.019-80, Rules of the technical operation of electrical consumers and Safety rules for operating electrical equipment.
There must be no moisture on the output terminals and the internal components of the device. It is forbidden to use the device in corrosive environments with acids, alkalis, oils , etc. in the air.
Mounting
Installation of device in housing Н
For installation of the device perform following actions:
Installation of wall-mounting device
  1. Fasten the bracket on the surface intended for mounting with three M4 × 20 screws (see Figure).
    Notice
    Screws for bracket are not included in the package.
  2. Hook the fixing bracket from the back panel of device to the upper edge of the wall bracket.
  3. Attach device to the bracket with the supplied screw.
Demount the device in the reverse order.
Notice
Remove the cover before wiring. Fasten the base of the device to the bracket with a supplied screw.
Dimensions of H housing
Notice
The bushings need to be cut in accordance with the diameter of the lead-in cable.
Installation of device in housing Щ1
Installation of panel-mounting device
  1. Prepare a place for mounting on the control panel (see Figure).
  2. Install the gasket on the frame of the device to ensure degree of protection IP54.
  3. Insert the device into a specially prepared hole on the front of the control panel.
  4. Insert the supplied retainers into holes on the sides of the device.
  5. Tighten supplied screws M4 x 35 in the holes of each retainer so that the device is pressed firmly to the front of the control panel.
Dimensions of Щ1 housing
Device in Щ1 housing mounted in the control panel with 3 mm thickness
Installation of device in housing Щ2
Disassemble the device in the reverse order.
Dimensions of Щ2 housing
Device in Щ2 housing mounted in the control panel with 3 mm thickness
Electrical connections
Wiring recommendations
To ensure the reliability of electrical connections it is recommended to use copper multicore cables, the ends of which should be carefully cleaned, tinned, otherwise use cable lugs before connection. Stripping of conductors must be performed in such way that the stripped ends after connecting to the device do not protrude beyond the terminal block. Cable cross section should be no more than 1 mm2.
General requirements for connection lines:
  • During the cabling, communication lines that connect the device with sensors must be isolated to a separate circuit (or several circuits) and placed separately from power cables or other sources of high-frequency and impulse interferences.
  • To protect the device inputs from the effects of industrial electromagnetic interference, the communication lines between device and sensors should be screened. Special cables with shielding or grounded steel pipes of suitable diameter can be used as screens. The cable shielding should be connected to the functional ground terminal (FE) in the control panel.
  • Network interference filters should be installed in the power supply lines.
  • It is necessary to install spark-suppression filters in the lines of switching of power equipment.
When mounting the system in which the device is used, the rules for effective grounding should be taken into account:
  • all grounding lines must be laid in Y-connected circuit, ensuring good contact with the grounding element;
  • all earthing circuits must be made with wires of the largest possible cross-section;
  • it is forbidden to connect the device terminal "Common" with grounding lines.
Getting Started
Danger
After unpacking the device, make sure that it has not been damaged during transportation.
If the device has been for a long time at a temperature below minus 20 °C, it is necessary to keep it in a room with a temperature corresponding to the operating range for at least 30 minutes before switching on and operation.
For connecting the device perform following actions:
  1. Connect the device to a power source.
    Caution
    Before powering up the device, it is necessary to check the correct connection of the supply voltage and its level.
  2. Connect the "device - sensors" communication lines to the sensors and to device inputs.
  3. Connect the "device - load" communication lines to the actuators and to outputs of the device.
  4. Apply power to the device.
  5. Set up the device.
  6. Power off the device.
Pin assignment
Screw terminals are located on the back wall of the panel-mounting device or inside the device (wall-mounting). The terminal block contacts assignment is shown in Figure.
Terminal block contacts assignments
Connection of switching devices and sensors
Caution
Supply voltage on the device inputs (pins 9 – 12 at the terminal block) must be in range from 0 to 24 V.
Notice
To supply the switching devices and sensors to the screw terminal block of the device is provided with supply voltage (pin 13 of the terminal block). If power consumption of input exceeds the load capacity of the built-in power supply (24 V), then an external power supply with an output voltage of 12 to 34 V (24 V recommended) must be used for powering.
Scheme for connection of the switching devices to the inputs is shown in Figures and .
Connection of "dry contact" switching devices
Connection of switching devices: a) for operation with n-p-n sensors; b) for operation with p-n-p sensors
Scheme for connection of passive and active sensors with an output n-p-n open-collector transistor or p-n-p is shown in Figures and accordingly.
Connection of n-p-n-sensors: a) active; b) passive
Connection of p-n-p-sensors: a) active; b) passive
Device has a dual switch for selecting, which of the types of sensors will work. It is located on the lateral side of the housing Щ1 and Щ2. For device in the H housing, the switch is located inside the housing (to access the switch, it is necessary to remove the device cover by unscrewing the four screws that fasten the cover to the base). Appearance of the switch is shown in Figure.
Dual switch
Positions of the switch depending on which device operates with different sensors, are shown in Table.
Switch status for different types of sensors
Type of sensors
Switch positions
n-p-n
1 – OFF↑; 2 – ON↓
p-n-p
1 – ON↓; 2 – OFF↑
Connecting load to the outputs
Outputs can be made in the form of electromagnetic relays (P), transistor (K) or triac (C) optocouplers. The outputs are used for direct load control (on/off) or for control by more powerful elements: contactors, solid state relays, thyristors or triacs. The outputs are galvanically isolated from the circuit of the device.
Scheme of connecting the load to the electromagnetic relay is shown in Figure.
Scheme of connecting load to the output of type Р
A transistor optocoupler is usually used to control a low-voltage relay (up to 50 V) – see Figure.
Caution
The diode VD1 (KD103 or similar type) should be installed in parallel to the relay coil, in order to avoid failure of the transistor due to the large self-induction current.
Scheme of connecting load to the output of type К
The optosimistor is connected to the control circuit of the power triac through the limiting resistor R1 according to the scheme shown in Figure.
Notice
Nominal value of the resistor determines the current of the triac.
Scheme of connecting a power triac to the output of type C
Optosimistor can also control a pair of anti-parallel connected thyristors (see Figure).
Scheme of connecting two anti-parallel connected thyristors to the output of type С
Caution
It is recommended to connect a filtering circuit (RC) to the terminals of thyristors or triacs in order to prevent breakdown due to high-voltage power surges in the network.
Operation of the device
Principle of operation
Functional diagram of the device is shown in Figure.
Functional diagram
The device has four independent digital inputs for external control signals. To the inputs can be connected:
  • switching devices (buttons, switches, reed switches, relays, etc.);
  • sensors with output n-p-n-transistor with an open collector;
  • sensors with output p-n-p-transistor.
The levels of the input signals are converted and processed in the matching unit and then sent to the digital signal processing unit that performs:
  • reassignment of inputs in accordance with the selected counting mode (see section);
  • filtering of input signals (see section);
  • counting incoming pulses on the device inputs;
  • convertion of the value from the counter into real physical value;
  • comparing signal value to the setpoint before displaying;
  • generation of signals for controlling the outputs according to a specified algorithm.
Control unit includes buttons for entering parameters of the device.
Display unit displays the measurement results or operating parameters on the indicators and shows the counter status using LEDs.
Secondary power supply converts the incoming voltage for all units of the device, depending on the version (with AC or DC power supply), and generates a signal indicating the loss of supply voltage.
The device can be connected with PC using RS-485 and USB interfaces that allow to set and edit the device configuration, monitor its current status and indications.
Control and indication
Elements of indication and control are located on the front panel of the device (see Figures and):
  • two seven-segment six-digit digital indicators, red and green – see Table;
  • six/eight LEDs (depending on the construction type) – see Table;
  • four/five buttons (depending on the construction type) – see Table.
All elements are placed on two (in housings Щ1 and Н) or on three printed circuit boards (in housing Щ2).
Graphic Graphic
Front panel of the device in housings for wall-mounting H and panel-mounting Щ1
Front panel of the device in housing for panel-mounting Щ2
Assignment of digital indicators
Indicator
Operating mode of the device
Displayed information
Upper indicator (red)
Operation
Current counter value
Setup
Name of the selected parameter
Lower indicator (green)
Operation
Setpoint value
Setup
Parameter value
LEDs assignment
LED
Status
Description
lights
Key lock is on
lights
Number of setpoint (1 or 2) that is currently displayed on the lower indicator
lights
Direct counting
extinguished (off)
Reverse counting
lights
Сurrently enabled output
Graphic*
lights
Input Reset is enabled
Graphic*
lights
Input Lock is enabled
Notice
* LEDs Graphic and Graphic are not available on the housing Щ2.
Buttons assignment
Button
Functions
Operation
Resetting (similar to incoming "Reset" signal on the device input)
Setup
Return previous (non-changed) value of the parameter during editing
Operation
Change the values of setpoints
Setup
  • Enter and exit the settings group
  • Enter the parameter editing mode and exit
  • Save the new parameter value in non-volatile memory of the device
Pressing at the same time buttons Graphic and Graphic and holding them for 2 sec opens access to configuration setup (PC-interface parameters).
Operation
Select the digit to edit when changing the parameter value or entering the password (used with the buttons Graphic and Graphic)
Setup
Graphic*
Operation
Setup
View parameter values and edit them,enter a password
Notice
* The button Graphic is not available on the housing Щ2.
Switch on and operation
During operation, the device counts the number of incoming pulses at its counting input, compares it with setpoint, converts this quantity into a physical value, and displays the value on the indicator. Device can operate in following modes of counting:
  • count-up;
  • count-down;
  • command;
  • individual;
  • reversing;
  • quadrature.
During operation the counter interprets different types of signals. On the device input first incoming pulse is considered as Start signal for counting. Counting stops when the Stop signal (next pulse) comes.
If there is an active "Reset" signal, the number of counted pulses is reset (counting continues from 0).
Block prevents the transmission of the counting pulses to the device input. While this signal is active, counting is blocked.
Caution
The setpoint is specified with the same accuracy as for counting physical values.. The multiplier can be set from 0.00001 to 99999. The conversion of counting results (result of multiplying) will be rounded up.
Read more about each of the counting modes, see section.
The counter also filters the input signals with two filters. The first one filters the signal on the counting input by pulse duration (from 1 to 50,000 Hz), the second filters signal on the control inputs of the device (from 1 to 999999 microseconds).
Setup
Sequence of setup
The Setup mode is intended for viewing and editing the device parameters. New parameters are saved to non-volatile memory of the device.
To enter (or exit) the Setup mode, press and hold button Graphic for at least 2 seconds.For access to configuration setup (parameters of connection with PC) press at the same time buttons Graphic and Graphic and hold them for 2 sec.
While editing, if no button is pressed within 2 min., device automatically restores previous value of the parameter and returns to parameter view mode. If within 3 minutes there are no actions in Setup menu, device automatically returns to Operation.
When device enters Setup for the first time, upper indicator shows PASS. Enter a new 4-digit password (default is 0000), save it and memorise. This password is further required for changing the device settings and for restoring factory settings (dEFAUL).
Notice
If you forgot your password, Setup mode can be entered with password 1098. When this value is entered, password is reset to 0000. Therefore, it is not recommended to set the new user password as 1098, because in this case, each time the password is entered, its value will be reset to default.
Structure of the device settings menu and sequence of pressing the buttons for setup is shown in figure and figure.
Device settings menu (beginning)
Device settings menu (ending)
Since the FDP and DP parameters set restrictions on each other (the number of displayed digits after the decimal point in the counting results can not be larger than the number of digits after the decimal point of the entered multiplier), editing of parameters FDP, DP, F should be performed in the following sequence:
  • to increase the number of displayed digits after the decimal point (decimal point offset to the left):
    • set parameter FDP;
    • set parameter F;
    • set parameter DP;
  • to decrease the number of displayed digits after the decimal point (decimal point offset to the right):
    • set parameter DP;
    • set parameter F.
Structure of the RS-485 configuration settings menu and sequence of pressing the buttons for setup is shown in Figure.
Notice
The list of configurable parameters of the device and their possible values is shown in Appendix.
RS-485 settings menu RS-485
Operating modes
Availiable types of counting (depending on the values of parameter inP) are presented in Table.
Types of counting
ModeDescription
Count-up
(inP = 1)
Input functions: Input 1 – count, Input 2 – start/stop, Input 3 – reset, Input 4 – block
Operating principle: Pulse count from zero upwards. When the setpoint is reached, the corresponding output is switched and the counter is reset
{t1–t2} – blocking signal the counting inputs;
t3 – switching of output 2 in case of coincidence of values of the counting register and setpoint 2;
{t4–t5} – stop-start signal;
t6 – switching of output 1 in case of coincidence of values of the counting register and setpoint 1
Count-down
(inP = 2)
Operating principle: Counting pulseopw6z7ds from the highest by the module setpoint to zero (decreasing). When the zero is reached, corresponding output is switched and the setpoint register is written to the count register
{t1–t2} – blocking signal on the counting inputs;
t3 – moment of switching of output 2 in case of coincidence of values of the counting register and setpoint 2;
t6 – moment of switching of output 1 in case of coincidence of values of the counting register and setpoint 1
Command count
(inP = 3)
Input functions: Input 1 – count, Input 2 - direction of count, Input 3 – reset, Input 4 – block
Two inputs are used: counting pulses are applied to the first, the status of the second determines the direction of the count. If there is a "logical 0" at the second output, the counter increases its value, if there is a "logical 1" it decreases. In this type two setpoints can be set, meanwhile:
• if the setpoints have the same sign, counter resets after reaching the setpoint, that is larger by module.
{t1–t2} – the decrease in the value of the counting register (impulse appears at the counting input 2);
t4 – moment of switching of output 1 in case of coincidence of values of the counting register and setpoint 1
• if the setpoints have different signs, the counter is reset after reaching each value
{t1–t3} – the decrease in the value of the counting register (impulse appears at the counting input 2);
t2 – moment of switching of output 2 in case of coincidence of values of the counting register and setpoint 2;
Notice
If the setpoint is set as zero, it is considered to be disabled, and the counter does not use it.
Individual count
(inP = 4)
Input functions: Input 1 – count 1, Input 2 – count 2, Input 3 – reset, Input 4 – block
Two counting inputs are used: pulses on Input 1 increase the value of the counting register, and the pulses on Input 2 decrease it. In this case, two setpoints are used (after reaching each of them, the corresponding output switches):
• if both setpoints have the same sign, counter does not reset after reaching lesser (by module) value. Otherwise, corresponding output is switched each time counter reaches this setpoint, regardless of the direction of the count
t1, t3, t5 – moments of the decrease in the value of the counting register (impulse appears at the counting input 2);
t.2 – moment of switching of output 2 in case of coincidence of values of the counting register and setpoint 2;
• if the setpoints have different signs (the first is greater than zero, and the second is smaller), then counter resets after reaching each setpoints
t1, t3 – moments of the decrease in the value of the counting register (the appearance of the pulse at the counting input 2);
Reversing count
(inP = 5)
Input functions: Input 1 – count 1, Input 2 – change counting direction (reverse), Input 3 – reset, Input 4 – block
After the power is on, the device is in the "count-up" mode by default. For reversing count it is necessary to apply signal to input 2.
Thus there are two counting inputs: pulses on Input 1, lead to an increase in the value of the counter, the counting direction is changed cyclically with each incoming pulse on Input 2. In this case, two setpoints are used (after reaching each of them, the corresponding output switches):
• if both the setpoints have the same sign
t1, t2 – moments of change of the counting direction (the appearance of the pulse at the counting input 2);
t1, t3 – moments of change of the counting direction (the appearance of the pulse at the counting input 2);
Quadrature / operation with encoders
(inP = 6)
The counting direction is determined by the meanders that come on two inputs. If the first meander is ahead of the second one, the counter counts the pulses at the first input in the increase mode, and if it lags – in the decrease mode. In this case, two setpoints are used (after reaching each of them, the corresponding output switches):
t1, t2, t5, t6 – meander at input 1 is ahead of the meander at the input 2,
the counter counts in the mode of increasing the value of the count register;
t3, t4 – the meander at input 1 lags behind the meander at input 2,
the counter counts in the mode of decreasing the value of the counting register;
t7 – moment of switching of output 2 for the time of exceeding the value of setpoint 2 by the counting register;
t8 – moment of switching of output 1 for the time of exceeding the value of setpoint 1 by the counting register
• if setpoints have different signs
t1, t2 – the meander at input 1 lags behind the meander at input 2,
t3 – moment of switching of output 2 in case of coincidence of values of the counting register and the setpoint 2;
t4, t5 – the meander at input 1 is ahead of the meander at input 2,
t6 – moment of switching of output 1 in case of coincidence of values of the counting register and the setpoint 1
Note
After reaching the physical limit of the count (if the counter does not reset after reaching the setpoint), the device transfers the overflow result and continues the count.
Configuring the device from PC
Device can be configured from PC by using RS-485 and USB communication interfaces. It supports three communication protocols: OWEN, MODBUS RTU и MODBUS ASCII. Addresses, names, dimensionalities, hash-codes and other configuration parameters are given in Appendix.
Functions of the software "Configurator СИ30" (file cfgSI30.exe), which is designed for configuring the device with PC, are described in the user manual "Pulse counter, model СИ30. Configuration" on the CD supplied. The configurator can be downloaded free from the website: www.owen.ru.
Parameters for reading indications of the counter from PC are described in Table.
Maintenance
Safety measures (see section) should be observed during the maintenance.
Maintenance of the device has to be carried out at least once in 6 months and includes the following procedures:
  • checking the mounting of the device;
  • checking the screw connections;
  • removing dust and dirt from the terminal block of the device.
Marking
The housing of the device is marked with:
  • name of the device;
  • protection class of the housing according to GOST 14254;
  • voltage and frequency of supply;
  • power consumption;
  • class of protection against electric shock according to GOST 12.2.007.0;
  • sign of type approval for measuring devices;
  • EAC sign;
  • country of origin;
  • serial number of the device and the year of manufacture.
Consumer packaging is marked with:
  • EAC sign;
Packaging
Device should be packed according to GOST 23088-80 into consumer packaging, made of paperboard (according to GOST 7933-89).
Packaging of the device for mail delivery is performed according to GOST 9181-74.
Transportation and storage
The device should be transported in closed vehicles of any kind. Packages should be fixed for transportation according to rules for corresponding type of vehicle.
Transport conditions must comply with conditions 5 in GOST 15150-69 (ambient temperature from minus 25 to +55 °C with observance of protection measures against impacts and vibrations).
Transportation should be carried out in individual packaging or in containers.
Storage conditions in containers on the warehouse of the manufacturer and consumer must correspond to conditions 1 in GOST 15150-69. The air must not contain aggressive admixtures.
The device should be stored on racks.
Scope of delivery
Item Quantity
The device 1 piece
Passport and warranty card 1 piece
User manual 1 piece
The verification procedure (at the request of the customer) 1 piece
Fasteners 1 set
CD with the software1 piece
Notice
The manufacturer reserves the right to make additions to the contents of the device.
Warranty
The manufacturer guarantees conformity of the device to requirements of technical conditions (ТУ) under the conditions of operation, transportation, storage and installation.
Warranty period of operation – 24 months from the date of sale.
In case of failure of the device during the warranty period at observance of conditions of operation, transportation, storage and installation the manufacturer undertakes to provide free repair or replacement.
Sequence of transmitting the device to service center is written in the passport and in the warranty card.
Device parameters
Configurable parameters
Parameter name and designation
Modbus address
Modbus function
Write / Read
Hash-code
Format, data size
Range of values and indication
Factory settings
Setpoint 1
U1
0×000C
0×000D
0×06, 0×10 / 0×03
0×FA1E
Long
(4 bytes)
from minus 99999 to 999999
999999
Setpoint 2
U2
0×000E
0×000F
0×06, 0×10 / 0×03
0×9707
Long
(4 bytes)
Counting mode
inP
0×0008
0×06, 0×10 / 0×03
0×38D9
Word
(2 bytes)
0 – Count-up (1)
Count-up
1 – Count-down (2)
2 – Command (3)
3 – Individual (4)
4 – Reversing (5)
5 – Quadrature (6)
Output mode
oUt
0×0009
0×06, 0×10 / 0×03
0×D11F
Word
(2 bytes)
0 – Switched after setpoint (1)
1 – Switched before setpoint (2)
2 – Switched for a time after the setpoint (3)*
3 – Switched when multiple setpoint values (4)
Notice
* After reaching the setpoint the output is switched for a time period, that is specified in parameteres t1  and t2, the count value is reset and the counting continues from zero (parameter SPM = RESET).
Time period for output 1
t1
0×0010
0×0011
0×06, 0×10 / 0×03
0×2E75
Unsigned long
(4 bytes)
from 0 to 999990 ms
1000 ms
Time period for output 2
t2
0×0012
0×0013
0×06, 0×10 / 0×03
0×436C
Unsigned long
(4 bytes)
from 0 to 999990 ms
1000 ms
Decimal point position multiplier
FDP
0×0014 0×06, 0×10 / 0×03 0×6ABF
Word
(2 bytes)
0 (------)
2 (----.--)
3 (---.---)
4 (--.----)
5 (-.-----)
Multiplier
F
0×0015
0×0016
0×06, 0×10 / 0×03
0×3085
Unsigned long
(4 bytes)
Position of the decimal point
DP
0×0007
0×06, 0×10 / 0×03
0×B3EB
Word
(2 bytes)
0 (------)
2 (----.--)
3 (---.---)
4 (--.----)
Type of work after reaching setpoint
SPM
0×000A
0×06, 0×10 / 0×03
0×69B2
Word
(2 bytes)
0 – Continue counting without resetting(CONT)
1 – Stop the counting until a "RESET" signal
(STOP)
2 – Reset the counter and continue counting
(RESET)
Type of work to "Reset" signal
rSt
0×000B
0×06, 0×10 / 0×03
0×4C9A
Word
(2 bytes)
0 – Reset the counter(1)
Reset the counter
1 – Reset the counter and disable output signals (2)
2 – Reset the counter and wait for signal "Start" (3)
3 – Reset the counter and wait for signal "Stop" (4)
Frequency of the input filter
FREQ
0×0017
0×06, 0×10 / 0×03
0×9FE6
Word
(2 bytes)
from 1 to 50000 Hz
50000 Hz
Minimum duration of the signal on the control inputs
Cnt.t
0×0018
0×0019
0×06, 0×10 / 0×03
0×5C98
Unsigned long
(4 bytes)
from 10 to 9999990 microseconds
10 microseconds
Input logic1)
(type of input signal)
SiG
0×001D
0×06, 0×10 / 0×03
0×601C
Word
(2 bytes)
0 – nPn
nPn
1 – PnP
Brightness of the indicator
brHt
0×001C
0×06, 0×10 / 0×03
0×0AE6
Word
(2 bytes)
from 0 to 3 (1 – 4)
Lock buttons
LoCK
0×001A
0×06, 0×10 / 0×03
0×E954
Word
(2 bytes)
0 – Buttons unlocked
(oFF)
Buttons unlocked
1 – Blocked counter reset (1)
2 – Change of setpoints is blocked
(2)
3 – Reset and change of setpoints are blocked (3)
Restore factory settings
dEFAUL
YES / no
Password
PASS
0×001E
0×06, 0×10 / 0×03
0×2728
Word
(2 bytes)
from 0000 to 9999
0000
Displayed setpoint2)
ind2
0×001B
0×06, 0×10 / 0×03
0×CAA0
Word
(2 bytes)
0 – Setpoint 1
1 – Setpoint 2
Command for applying settings2)
APPL
1 – Exit with saving
2 – Exit without saving
3 – Return to factory settings
RS-485 settings
RS-485 data transfer rate
bPS
0×0000
0×06, 0×10 / 0×03
0×B760
Word
(2 bytes)
0 – 2400
9600
1 – 4800
2 – 9600
3 – 14400; 4 – 19200
5 – 28800; 6 – 38400
7 – 57600; 8 – 115200
Data word length
LEn
0×0001
0×06, 0×10 / 0×03
0×523F
Word
(2 bytes)
0 – 7 bit (7 bit)
8 bit
1 – 8 bit (8 bit)
Parity
PrtY
0×0002
0×06, 0×10 / 0×03
0×E8C4
Word
(2 bytes)
0 – Without parity (NO)
Without parity
1 – Even parity
(EVEN)
2 – Odd parity (Odd)
Number of stop bits
Sbit
0×0003
0×06, 0×10 / 0×03
0×B72E
Word
(2 bytes)
0 – 1 stop bit
1 stop bit
1 – 2 stop bits
Base address of the device3)
Addr
0×0005
0×06, 0×10 / 0×03
0×9F62
Word
(2 bytes)
from 0 to 255 when A.Len = 8
16
from 0 до 2047 when A.Len =  11
Length of network address2)
A.LEN
0×0004
0×06, 0×10 / 0×03
0×1ED2
Word
(2 bytes)
8 bit
8 bit
11 bit
Response delay
RS-485
rS.dL
0×0006
0×06, 0×10 / 0×03
0×CBF5
Word
(2 bytes)
from 0 to 45
Notes
1) Setting of parameter SiG works only together with DIP switch (see section).
2) Parameters that are not displayed in the Setup mode of the device.
3) In Modbus protocol address 0 is reserved for broadcast packages. In OWEN protocol address 255 is reserved for broadcast packages.
Readable parameters
Designation and parameter name
Modbus address
Modbus function
Read-only
Hash-code
Format and size of data
Note
Current value of the pulse counter Ctr
0×0000
0×0001
0×04
0×A158
Long (4 bytes)
Current counter value in physical units CEU
0×0002
0×0003
0×04
0×B8BC
Long (4 bytes)
Current status of the "Start/stop"
StSt
0×0004
0×04
0×6577
0 – start;
1 – stop
Current mode (count, setup)
CUR
0×0005
0×04
0×CC41
Word (2 bytes)
0 – count (password not required);
1 – setup from the device's buttons;
2 – setup from the PC;
3 – count (requires password)
Network error code on last access
to the device
n.Err
0×0006
0×04
0×0233
Word (2 bytes)
From 0 to 255.
After turning on the device – 0
Name of the device
DEV
0×0007
0×0008
0×04
0×D681
ASCII string
(4 bytes)
Software version
VER
0×0009
0×000А
0×04
0×2D5B
ASCII string
(4 bytes)
X.YY,
where Х – number of version, YY – number of subversion
Bit parameters
Designation and name of parameter
Modbus address
Modbus function
write / read
Hash-code
Note
Digital inputs
Current status of the "Reset" input
rSti
0×0000
– / 0×02
0×C010
Byte (1 byte)
0 / 1
Current status of the "Block" input
Loci
0×0001
– / 0×02
0×93EC
Byte (1 byte)
0 / 1
Digital outputs
Status of output 1
OSt1
0×0000
– / 0×01
0×6FFD
Byte (1 byte)
0 / 1
Status of output 2
OSt2
0×0001
– / 0×01
0×52A1
Byte (1 byte)
0 / 1
Reset of counter
rStC
0×0002
0×05, 0×0F / 0×01
0×DF1F
Byte (1 byte)
0 / 1
0 – no action;
1 – reset
Enable/disable the program control mode counter START/STOP
OnOff
0×0003
0×05 / –
0 – OFF (0x0000);
1 – ON (0xFF00)
Command to set the program control mode counter START/STOP
PStSt
0×0004
0×05 / –
0 – STOP (0x0000);
1 – START (0xFF00)
